所以说可以在墙上做一个挂钩,将门固定住不让其掉下来就可以了。
如果你换智能电表 光这样就不行了
背板也要装合页能开合
The space must:
a) Be flat and level
b) Enable the door or panel to be opened or
removed; and
c) Provide a vertical clearance of not less than
2 metres from the ground, platform or floor
and minimum horizontal clearance of not
less than 0.6 metre from the:
i) Equipment mounted on the hinged
panel; or
ii) External front edge of the switchboard
enclosure
whichever point protrudes the most.
A hinged meter panel must be able to be
extended to a 90° open position when all
equipment has been fitted.
When a hinged meter panel is extended on its
hinge to the 90° open position, make sure a
clearance of 200mm is maintained between the
front face of the panel and any fixed object.
Recessed enclosures are to maintain a
minimum of 50mm clearance from the building
to enable installation of communications
equipment.
Provide a clearance of 175 mm from the front of
the panel to the door.
Note: The local government Act requires
compliance to the Building Code of
Australia for exits for fire escape
purposes, or any corridor, hallway, lobby
or the like leading to such an exit. This
does not apply in single dwellings. In the
case of buildings being altered or the use
being changed, the local council may
require an existing building to be brought
up to this standard. |